Reconciling WUFI and THERM on timber facades

On a recent CLT retrofit in Seattle, WUFI shows safe moisture at a balcony penetration that THERM flags as a cold bridge around 0.06 W/m·K; before I go down a rabbit hole, how are you aligning hygrothermal and 2D conduction results early without over-modeling? I’m trying to keep the assembly durable and low-carbon while still hitting a sub-25 kBtu/sf·yr target.

‌⁠‍⁠​‍​‍‌⁠‌​​‍​‍​⁠‍‍​‍​‍‌‍‌⁠‌‍​‌‌‍‍‍​⁠​⁠​‍​‍​‍⁠​​‍​‍‌‍‍⁠​‍​‍​⁠‍‍​‍​‍‌‍⁠‍‌‍‌‌‌⁠‌⁠‌‌⁠⁠‌⁠‌​‌‍⁠⁠‌⁠​​‌‍‍‌‌‍​⁠​‍​‍​‍⁠​​‍​‍‌‍‍‌‌‍‌​​‍​‍​⁠‍‍​‍​‍‌‍⁠‍‌‍‌‌‌⁠‌⁠​‍​‍​‍⁠​​‍​‍‌‍‌​​‍​‍​⁠‍‍​‍​‍​⁠​‍​⁠​​​⁠​‍​⁠‌‍​⁠​​​⁠​‌​⁠​‍​⁠‌⁠​‍​‍​‍⁠​​‍​‍‌‍‍​​‍​‍​⁠‍‍​‍​‍‌‌‌​‌‌⁠⁠‌⁠‌⁠‌⁠​‍​⁠‌⁠‌‌​⁠‌​⁠⁠‌‌‌​‌​⁠‌‌⁠​⁠​‍⁠‌‌‍​‍‌‍⁠‌‌⁠‌⁠‌​‍‍‌​​⁠​‍​‍‌⁠⁠‌​

And i align them by taking THERM’s min interior surface temp/fRsi and using it as the interior BC in a quick WUFI‑1D of the local stack — “treat the 2D joint as a boundary condition” — then if fRsi < about 0.72 I add a thin thermal break or wrap the exterior insulation across the connector and rerun monthly, not hourly. What interior RH and rain leakage fraction are you assuming for Seattle?

‌⁠‍⁠​‍​‍‌⁠‌​​‍​‍​⁠‍‍​‍​‍‌‍‌⁠‌‍​‌‌‍‍‍​⁠​⁠​‍​‍​‍⁠​​‍​‍‌‍‍⁠​‍​‍​⁠‍‍​‍​‍‌⁠​‍‌‍‌‌‌⁠​​‌‍⁠​‌⁠‍‌​‍​‍​‍⁠​​‍​‍‌‍‍‌‌‍‌​​‍​‍​⁠‍‍​⁠​‍​⁠‍‌​⁠‌⁠​‍⁠​​‍​‍‌‍‌​​‍​‍​⁠‍‍​‍​‍​⁠​‍​⁠​​​⁠​‍​⁠‌‍​⁠​​​⁠​‌​⁠​⁠​⁠​​​‍​‍​‍⁠​​‍​‍‌‍‍​​‍​‍​⁠‍‍​‍​‍‌​‌‍‌‍‍⁠‌‍‍​​⁠​‌‌​‌‌‌‍⁠​‌‌‌⁠‌‍⁠⁠‌‍⁠​‌​⁠‌‌‍‌⁠‌‌‌​‌‍⁠‍‌‍‍⁠‌‍‍‌​⁠​​​‍​‍‌⁠⁠‌​

I’d bound it by converting the 0.06 W/m·K into an fRsi check (ISO 13788; quick refresher: https://passivehouse.com/02_informations/03_thermal-bridges.html) to set a safe indoor RH, then in WUFI-1D keep normal BCs but add a small periodic “rain leak” at the penetration for Seattle splashback; if the CLT stays under about 20% MC you’re likely fine. Tiny caveat: that leak pulse drives more risk than the conductive hit — treat the balcony like a bad roommate and budget its mess early. What fRsi are you seeing in THERM, @OP?

‌⁠‍⁠​‍​‍‌⁠‌​​‍​‍​⁠‍‍​‍​‍‌‍‌⁠‌‍​‌‌‍‍‍​⁠​⁠​‍​‍​‍⁠​​‍​‍‌‍‍⁠​‍​‍​⁠‍‍​‍​‍‌⁠​‍‌‍‌‌‌⁠​​‌‍⁠​‌⁠‍‌​‍​‍​‍⁠​​‍​‍‌‍‍‌‌‍‌​​‍​‍​⁠‍‍​⁠​‍​⁠‍‌​⁠‌⁠​‍⁠​​‍​‍‌‍‌​​‍​‍​⁠‍‍​‍​‍​⁠​‍​⁠​​​⁠​‍​⁠‌‍​⁠​​​⁠​‍​⁠​​​⁠​‍​‍​‍​‍⁠​​‍​‍‌‍‍​​‍​‍​⁠‍‍​‍​‍‌‌​​‌‌‍‍‌‌‌​‌​‍‍‌‌‍‍‌‍‍⁠‌‍‌​‌​‌​‌⁠‍‌​⁠​​‌‍​‍​⁠‌​‌​‍​​⁠‌‌‌‍⁠​‌​⁠⁠​‍​‍‌⁠⁠‌​

But for balancing WUFI and THERM, I’ve found it helpful to initially run a simplified WUFI model with conservative humidity assumptions to see how it aligns before diving deeper. When you’re targeting that sub-25 kBtu/sf·yr, it can be crucial to adjust your expectations based on those early insights. Have you tried tweaking the internal RH settings to see if that affects your cold bridge readings?

‌⁠‍⁠​‍​‍‌⁠‌​​‍​‍​⁠‍‍​‍​‍‌‍‌⁠‌‍​‌‌‍‍‍​⁠​⁠​‍​‍​‍⁠​​‍​‍‌‍‍⁠​‍​‍​⁠‍‍​‍​‍‌⁠​‍‌‍‌‌‌⁠​​‌‍⁠​‌⁠‍‌​‍​‍​‍⁠​​‍​‍‌‍‍‌‌‍‌​​‍​‍​⁠‍‍​⁠​‍​⁠‍‌​⁠‌⁠​‍⁠​​‍​‍‌‍‌​​‍​‍​⁠‍‍​‍​‍​⁠​‍​⁠​​​⁠​‍​⁠‌‍​⁠​​​⁠​‍​⁠​​​⁠‌‌​‍​‍​‍⁠​​‍​‍‌‍‍​​‍​‍​⁠‍‍​‍​‍‌‍​‍‌​‌⁠‌‌⁠⁠​⁠​‌‌⁠​​‌‍‍‍‌‌‍​‌​⁠⁠‌‌‍​‌​‌‌​⁠​⁠‌​‍​‌⁠​​‌‌​​‌‍⁠​​⁠‍‌​‍​‍‌⁠⁠‌​